Did you or the guy did UPS self diagonistics?
He didn't do anything.
Watt is a unit, not a measured quantity. The equation is P = I * V (power = current * voltage), but even this only applies to resistive loads in a DC circuit. That's why you see UPS rated at VAC(with approximate some watt rating).
- - - Updated - - -
Try my method pick 3 100W filament bulbs(Rs.10-15 each) and connect to the UPS and run and see how long it lasts.
this
Ok. I'll see about this. My UPS is on charge since morning. By the time I get back home it should already be on charging for 11 hours.
However, it did provide 20 mins backup on idle/light usage so I doubt the batteries are at fault.
Yes charge the UPS for at least 12 hours and then see if it is giving backup or not because when I bought my APC 600VA it wasn't giving me any backup but after several hours of charging now its working normally as my max requirement is 480w including the monitor.
Like I said, it does provide backup when the system is idle.
A 500W 80+ bronze certified PSU's power draw @100% load will be calculated like
Active power factor correction = .9 (most consumer PSU have this rating)
500/(.81*.9) = 686VA
80+ bronze is atleast 81% efficiency
Do you mean VA or Watts here?
So you mean to say that if my system components take 300W(going by anandtech's calculation of 270-280W + adding 20-30 watts on it) it is effectively drawing 300/(0.81x0.9) = ~412W from the UPS? Add another 30W of the monitor and 6W from the Router and another 5W for any variance as such it is still 453W.
Now if the UPS itself is 90% efficient then we have a problem. If it is designed to give 480W then I should be okay.
PS - my PSU states 87% efficiency so that should be under 400W.
I'm sure I'm cutting it close because the UPS has that clicking sound which seems like it just exceeds the threshold within seconds and shuts down. Perhaps if I had like 25W lesser I wouldn't face this problem? (Just guessing)