So you say Seasonic S12II Series PSU = Corsair VS Series PSU since I am getting the same problem. What do you say Harshil???
I never said S12II has any problem.
So you say Seasonic S12II Series PSU = Corsair VS Series PSU since I am getting the same problem. What do you say Harshil???
I never said S12II has any problem.
This should help you found this after some searching
Weird Power Issue [PSU/UPS]
According to this at max load
520Watts PSU
80% Efficient
so the maximum my SMPS may draw is 520x100/80 = 650 Watts
Bear in mind, its 650Watts and not 650VA
a modified sine wave has a power factor on 0.6
650/0.6 = 1083.33va
So you may need to change the ups
This should help you found this after some searching
Weird Power Issue [PSU/UPS]
According to this at max load
520Watts PSU
80% Efficient
so the maximum my SMPS may draw is 520x100/80 = 650 Watts
Bear in mind, its 650Watts and not 650VA
a modified sine wave has a power factor on 0.6
650/0.6 = 1083.33va
So you may need to change the ups
I tried a modified BIOS and lowered the voltage from default 1.238V to 1.156V. Also reduced the core clock from 1070 to 950 MHz. Tried running Unigine Heaven and turned off the mains. A very shaky alarm tone came from the UPS and it shut down within 5-7 seconds.
There is no way the system is even drawing 300W. Please check the HIS R9 270's power consumption here - AnandTech Portal | The AMD Radeon R9 270X & R9 270 Review: Feat. Asus & HIS.
Its 239W. My voltage is even below what HIS has. I should not be drawing more than 250W at max.
Also, if its the sinewave thing, shouldn't the PC shut down when I'm not playing games and the lights go off? Then it works fine.
Should I contact APC?
- - - Updated - - -
Damnit, that means I need an APC 1100VA. Totally broke now. :-/
Also, if its the sinewave thing, shouldn't the PC shut down when I'm not playing games and the lights go off? Then it works fine.
Should I contact APC?
According to this at max load
520Watts PSU
80% Efficient
so the maximum my SMPS may draw is 520x100/80 = 650 Watts
Bear in mind, its 650Watts and not 650VA
a modified sine wave has a power factor on 0.6
650/0.6 = 1083.33va
So you may need to change the ups
tried to contact apc.
his system will never push the psu to maximum load.
It's simply a compatibility problem between that PSU and that UPS. Neither Back-UPS nor Back-UPS Pro gives pure sine wave. You'll need an even higher variant. Try to sell that PSU and get an S12II.
Anyways, contact APC about this too and see if they can do anything.
I am using a s12II 620 with APC 1.1kVA. Although I had some random UPS shutdown even when main supply was online, never faced any problem while gaming on battery. For my problem I contacted APC customer support and they were very helpful. Although they and myself are yet to figure out what caused the shutdowns the problem vanished as it came. My assumption is the battery was not fully charged and due to voltage fluctuations the UPS went to battery mode and tripped everytime in my Case. Contact APC support. There are some very helpful guys out there.
This is what was written on xBit Labs -^ The M12II is a modular S12II with a different PFC. You cna google for more details on 'M12II with stepped appriximated UPS' and you'll find details. I don't remember the page bit it said S12II 430, S12II 520 and M12II all have different PFC modules.
i wont advice you to sell the psu. let us see what apc can offer.
...... the UPS's beep sounded like it was ill or dying and I could also hear a lot of 'tut' 'tut' sounds from it before it finally shut down (in 50 seconds flat).
.....
Nothing. The guy comes and says I need a 1500VA UPS. Too much load.. I told him its not even 350W. He says "wo nahi chalega Sir. Kuch bhi karo, nahi chalega. 480W likha hai output par nahi chalega"
What do i do now? Complain to APC again?
I don't agree with APC having stellar customer support.
Nope, he did nothing.. I just started Bioshock infinite and turned off the mains.. BAM! the UPS trembled,, "tit tit" sounds could be heard and then.. and then..my friends.. the inevitable happened..Probably your batteries are bad. 800VA UPS should atleast give backup to your config for 5 mins(assuming 2x12V 7Ah batteries inside).
Did the APC guy check the batteries??