Now you now see how hold up time is highllllllyyy unlikely to be the cause
Thanks for that link , a much more detailed proof for what I have said
Please read that and my replies again
I have said exactly the same thing they are saying
Here
the inrush current required by the PSU
could easily exceed the maximum current output capacity of the UPS inverter, forcing the UPS to shut
down to protect its own inverter components.
It's after this statement they are saying what you have bolded
As a result, Eaton recommends using a UPS with a transfer time of less than 5 ms, if the UPS will be
loaded to 70 percent or more of its capacity. Rapid transfer time helps prevent a UPS overload condition
that could cause a system failure
They are trying to not overload the UPS of a given size , when it will be running at a higher load of"70% or more ".. [ deliberately fixing 1 part of the equation ] the only way to do this is by shortening transfer time, and thus reducing inrush current as a result of not allowing caps to discharge heavily , which is what I have said previously
Or you can have a long transfer time of ups at the cost of higher inrush current ( means higher VA UPS required to avoid overload )
Now that less than 5ms Transfer time of UPS is highly difficult to get .. Plus they are mainly talking about high loads
Look at apc 600va it has transfer time of 4-8ms typically , that less than 5ms figure will be achieved rarely ,maybe 2-3 times out of 10.. and afaik as i said it depends at what point on sinecurve does the AC power is lost.. Purely luck based afaik
So the only realistic solution is to get a higher VA UPS to sustain higher inrush current with normal higher transfer times of general decent ups
The actual inrush current will vary from PSU to PSU , PC load , how much cap discharged , other things etc and cannot be ascertained without proper testing ..
All we know
1)his other psu is drawing less inrush at full load than what his UPS can handle..
2) While at low load his new psu's inrush current is within limits of his UPS , but not at high load
3) While his invertor has enough headroom to support higher inrush of PSU at full load , that is why it works fine
So this is why I was saying that there are good chances that 600 VA apc can work (""maybe"" much better threshold to power inrush, ""much"" shorter transfer time , thus ""less inrush current""
but still there is risk involved , and may not work , so make pre arrangements to return in case it doesn't work..
Cannot be determined without trying or without having proper measurements
Read the apc faq i linked previously again
Computers containing PFC (Power Factor Corrected) power supplies and their use Back-UPS and Smart-UPS SC with Step Approximated Sine waves.
They say the same thing
chimera201 said:
Now this is where you are wrong. You assume the transfer time of the iball UPS as advertised.
No , i didnt assume at all
Please read again
That 8ms figure I was taking as "hold up time" of PSU as worst case scenario at full load .. And showing how his hold up time at his pc load will easily exceed 25ms in even worst case scenario.. In reality it will be higher since his load will be slightly less than 150 watts at full load + his PSU has a higher hold up time than that.. Although it can vary a little bit from unit to unit as caps aren't exactly precise to the specs everytime