Mercury UPS problem !! help me

femin

Right off the assembly line
Last week my UPS got repaired, Its classic 600VA Ups , the problem is when the main power is on it gives output and when main is off then the UPS gone to off , battery power is not consumed , the battery is 100% at good condition , can u support me , and i think a problem in relay and i changed two relay but the problem still exists , if i turn on the ups at battery power its getting turned on and immediately going to off !!! kindly support me to repair it , battery is working good with other UPS, problem is with the UPS
 

thetechfreak

Legend Never Ends
you are probably overloading it by connecting all components of your computer with it.
Please post your computer config.
 
OP
F

femin

Right off the assembly line
no overloading , i 'm using AMD athlon x2 dualcore 2.8Ghz and 3GB DDR2 memory with 2TB HDD , i connected my speakers and monitor in my home inverter .. battery is a new EXide
 

thetechfreak

Legend Never Ends
so you are not overloading it. Are there too many voltage fluctuations in your area? You do have proper Earthing?
 
OP
F

femin

Right off the assembly line
so you are not overloading it. Are there too many voltage fluctuations in your area? You do have proper Earthing?

no voltage problem , problem is in the board , i replaced the 4 relay but still problem exists , my guess the problem is in the battery meter (the component which shutdown the ups while the battery is low), cas if i short a capacitor the UPS is working fine , but the capasitor is in good condition cas i replaced it with new ,
 